[ale] OT: question about replacing batteries in a APC UPS
James P. Kinney III
jkinney at localnetsolutions.com
Wed Dec 21 20:13:32 EST 2005
Mike: Great instructions. An easier method is to test with on of the $13
at Home Depot outlet testers. It has 3 lights that indicate all good,
open ground, open common, reversed polarity (hot swapped with common) or
fatal nightmare of hot swapped with ground (this will KILL a UPS). It
can't test the ground to cold water pipe path though so keep that test
around.
On Wed, 2005-12-21 at 10:30 -0500, Mike Harrison wrote:
> Courtney asked:
> > What and how do the testers reveal ?
>
> Disclaimer: This is potentially dangerous, don't touch anything metal,
> don't wear shoes with metal tacks in the heels.. don't.. (it's a long list)
>
>
> Good question. Set to AC Volts, (Alternating Current) you can test an
> outlet as follows:
>
> The outlet should have 3 plugs.. 2 slots, one larger than the other
> and a round hole:
>
> [ |
> o
> The larger slot on the left is 'neutral' the smaller one on the right
> is 'line' or 'hot' and the small circle is 'ground'.
>
> In a perfect world. 'hot' has a sine wave of approximately 117 volts
> calculated as a 'root mean square' average of alternating electrical
> potential. You want to make sure it's there, and that 'neutral' is
> at 0 volts, as is ground.
>
> So with your el-cheapo voltmeter, stick the probe tip black lead in
> the 'neutral' and the red lead into 'hot'. You should get 110 to 120 volts AC.
>
> Then move the red lead into 'ground'. You should get 0 volts. Maybe 0.5volts.
> but it should be 0. Ground and neutral (in most systems) tie into the
> same place back at the breaker panel.. they should have the same
> potential.
>
> Then move the black lead to 'hot'. You should get 117 volts. If not,
> your ground is open, not grounded. Very common problem in houses.
> The purpose of the ground wire is safety. The metal chassis of a
> device uses the ground wire as a redundant path back to the breaker
> box. If there is 'leakage' via EMF from high voltage electronics
> or transformers or.. (lots of things), it should drain down the
> ground wire. If it is 'open', a shock potential from the device may
> exist. Grounds are also a catastrophic failure protection means.
> If a power supply 'melts down' and shorts to ground, the current
> should travel back to the break panel at close to 0 volts, and if the
> current level is high enough, allow the breaker to trip.
>
> Last test: paranoid mode. If you have something that is grounded
> handy, like a metal copper pipe that goes into the earth, large metal
> structural supports.. etc.. - Measure between it and the Ground and
> Neutral and make sure it's 0 volts or really really close to it. (.5volt?)
> and measure between the natural earth ground and 'hot' you should get
> 110-120 volts.
>
> So.. If all is good, you have a properly wired electrical outlet, there is
> one good 'idiot check' you can make on your UPS:
>
> Set your meter to Ohms. A measure of electrical resistance.
>
> With your UPS unplugged, put the black lead on the round pin.
> then put the red volt meter lead on any metal on the case.
> It should be under 1 ohm. Now move the red lead to the round
> plug hole on the outlets. Same thing. 1ohm or less.
>
> On some UPS's you MAY be able to do this with 'hot' and 'neutral' on
> the outlet to the cord plug end for hot and neutral, depends
> if it's using a relay for power pass through and what it's position
> is when 'off'.
>
> Plug your UPS in and turn it on. Repeat the first set of steps for the
> outlets on the UPS.
>
> Last test. turn off the power to the UPS, but keep it plugged in (so
> ground is still attached) so that the UPS is running on batteries.
> It may work better if something is plugged in and running off the UPS
> as many of them require a load. Then do the tests again. You will get
> something approximating 110-140 volts from neutral to line on the UPS, it
> depends on the quality of the site wave your UPS generates. It may read
> high if there is no load or a very small one, and/or it produces a squarer
> waveform than normal line power.
>
> ----------------
>
> Honest disclaimer: I've done these tests and more.. but I usually
> just plug them in and see if they work. :) - I did check out the wiring in my house
> when I bought it for proper polarity of the pins, and good grounds..
> and again when I put in the generator and UPS's.. but I'm insane.
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
> _______________________________________________
> Ale mailing list
> Ale at ale.org
> http://www.ale.org/mailman/listinfo/ale
--
James P. Kinney III \Changing the mobile computing world/
CEO & Director of Engineering \ one Linux user /
Local Net Solutions,LLC \ at a time. /
770-493-8244 \.___________________________./
http://www.localnetsolutions.com
GPG ID: 829C6CA7 James P. Kinney III (M.S. Physics)
<jkinney at localnetsolutions.com>
Fingerprint = 3C9E 6366 54FC A3FE BA4D 0659 6190 ADC3 829C 6CA7
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: application/pgp-signature
Size: 189 bytes
Desc: This is a digitally signed message part
More information about the Ale
mailing list